View Single Post
  #7  
Old 9th September 2022, 09:58 AM
ainarssems ainarssems is offline
Senior Member
 
Join Date: Aug 2010
Location: Rushden, Northants
Posts: 3,806
Default

Quote:
Originally Posted by Conan_the_Librarian View Post
Thanks for the replies peeps. Looks like I need an export limiter to stop the batteries being drained. Set it to zero or a nominal figure and during the day it will provide the difference between what the house needs and what the PV is supplying. When there is no sun it can provide upto the 5Kw rating and if more is needed when there is no sun, the grid supplies the rest. If the PV is supplying more than is needed then the export limiter sets the hydro inverter to zero and the charge controller uses the dump load to protect the batteries from over charge and the generator from damage. At night on low load it allows the hydro inverter to supply only what the house needs. This way I don't breech the export limit of 4Kw. I think!
Normally the export limiter is not a separate device but the function built into inverter you just need to connect measuring device (meter or CT clamp) attached to your mains cable from grid or meter tails that provides data to inverter. It just reduces generation amount when it reaches export limit. Other option would be power diverter which would send extra power to something like a heater in which case inverter will still be working at full power and diverter just dumping extra generation in the heater. If you can see all your stats for import, export and grid consumption then you must already have suitable measuring device in place. And most modern inverters have setting for limitation.

If you have permission to connect 4kW it does not mean that you can install more when you feel like and just limit export to 4kW or less. You still need to apply for connecting more equipment each time you connect anything extra highlighting any proposals how you will limit the export. Usually it is just a wiring diagram showing metering device connected to inverter and if it's TYPE tested inverter just giving them the inverter make and model and stating that it will be configured in inverter settings. Do you know what inverter you have?

Quote:
Reasoning failed! The fact that 32 of the customers live in park homes that aren't allowed PV or wind generators as a T&C of their leases and 4 of the houses are surrounded by trees or don't have a roof suitable then the last two who both have PV are still limited to 4Kw systems.
There is a bit more to this than just a number of houses and how many have or will have panels. The transformer is 3 phase and and if all 3 houses are connected to the same phase or even 2 to 1 phase and 1 to another phase it may cause phase imbalance with voltage going above maximum specs on the phase that receives most of generation. If it just happen that each of the houses were on different phase then there would be no reason for a low limit so it all depends on individual circumstances.

With DC charger and 3/4 different systems you might have some issues with them talking to each other and working nicely together and not yoyoing up and down trying trying to adjust. Ideally you would need some kind of central control unit that makes decisions and sends instructions to each device, this could be local or cloud based but it might be difficult if they are not from the same manufacturer. When I was 1st looking Victron range looked promising with local gateway that you can connect all your controllers to. At the end for simplicity and tidier installation I went with single unit hybrid solar/battery inverter, charger and battery enclosure and batteries.
This is what I got but the demand has gone up since and it's harder to get them now with either out of stock or long waiting times and price has gone up by about 20% as well https://www.itstechnologies.shop/col...ttery-98-d-o-d the picture on this link shows older model but they shipped the latest version which you can see here https://www.fox-ess.com/all-in-one/

I think what I would do is connect hydro permanently to mains without any limitation as it cannot exceed your limit. If your solar inverter support limitation use meter or CT clamp to measure incoming/outgoing from grid and set limit to 4kW or less.
Then use AC coupled battery storage with meter or CT clamp and it will take care of itself, when it will see export and battery not full it will adjust battery charge power automatically to keep export close to 0. If the battery is full and stops charging the power will go to grid if the inverter sees that you are getting close to export limit it will reduce generation. When it will see import and battery not below discharge limit it will generate electricity to keep your import close to 0. It will always try to keep import/export as low as possible. with AC storage you don't need your devices to talk to each other you just need import/export data from meter or CT clamp.

If your current inverter does not support limitation you could either replace inverter with the one that does and get AC coupled storage or replace it with hybrid solar/battery inverter with integrated charger. With the AC coupled charger or hybrid inverter/charger you also have option to charge the battery from grid during night when electricity is cheaper and then use during day when it is more expensive but you will probably not need it if you are looking to generate 1000W+ hydro in winter

Instead of limiting what inverter generates you could chose to divert extra generation to heating but in winter when you need heating most you are unlikely to have much excess generation and if you are just going to heat water during summer I am not sure it's worth it. I just chose to charge car with excess power. It may involve a bit of planning ahead for example if I see good weather ahead but will not be at home at the time I may chose to charge car from the battery and then let the battery recharge when sun comes out.
__________________
Currently 8less
2011 Q7 S Line 3.0TDI, 2016 Tesla Model S 90D

8 history:
2006 A8 Sport 4.2TDI quattro SOLD,
1997 S8, reached end of life with gearbox failure
Reply With Quote